Error Code Display

The following table is only valid if the fault indicator is constantly on and the status indicator is flashing red.

If the fault indicator is flashing the module requires a firmware update or is currently in firmware update mode.

The status indicator will flash red with the error code number. The error code number is shown with a 250ms on and off period (duty cycle) with a delay of 1.5 seconds between each display cycle.

Flash

Error Description

1

Unknown Error Code

The error code returned by the system controller could not be understood by the module.

2

Firmware Version

The firmware version on the module is not compatible with the system controller. To clear this error, update the module using the module update feature in the controller's web interface.

3

Address Too High

The module address is above the maximum number available on the system controller. To clear this error change the address to one within the range set on the system controller, restart the module by disconnecting the power.

4

Address In Use

The address is already in use by another module. To clear this error set the address to one that is not currently occupied. Use the view network status command to list the attached devices, or the network update command to refresh the registered device list.

5

Controller Secured Registration Not Allowed

The controller is not accepting any module registrations. To allow module registrations use the network secure command to change the setting to not secured.

6

Serial Number Fault

The serial number in the device is not valid. Return the unit to the distributor for replacement.

7

Locked Device

The module or system controller is a locked device and cannot communicate on the network. Return the unit to the distributor for replacement.